- Applications & Use-cases
- Detailed Specifications of NCD's Uptime Monitor
- Getting started
- Node-RED Dashboard
- Advanced Configuration
- Read Sleep Duration
- Read Sensor Network ID
- Appendix A - Configuration Commands
- Appendix B - Command Acknowledgement Data
- Appendix C - Application Specific Commands
- Appendix D - Error Code Descriptions
- Appendix E - Frame Checksum Calculation
- Industrial Grade Machine Uptime MonitoringÂ
- Measure Production Uptime
- Measure Number of Cycles
- Dry Contact Closure Input
- Wet Contact Closure Input
- Acceleration Motion Detection based Uptime calculatorÂ
- Magnetic Field Detection based Uptime calculatorÂ
- Current-based Uptime calculatorÂ
- Humidity Range 0-90%
- For Indoor and Outdoor Use
Table of Contents
This sensor is a versatile device that brings a new level of precision and reliability to uptime monitoring across a wide range of industrial applications. Its unique combination of digital and analog sensing technologies, coupled with robust wireless communication and a durable enclosure, makes it an ideal choice for diverse environments and challenging operational conditions.
Applications​
 Manufacturing Plants
In manufacturing settings, the ability to monitor machine uptime accurately is crucial for minimizing downtime and maximizing productivity. The sensor’s multi-sensor functionality enables detailed tracking of production uptime and cycle counts. Its dry and wet contact closure inputs, along with current-based, acceleration motion detection, and magnetic field detection-based uptime calculators, provide a comprehensive view of machine performance. This ensures manufacturing plants can swiftly identify and address issues, maintain high operational standards, and optimize production schedules.
Automotive Production Lines
Automotive manufacturing demands high precision and efficiency, where any interruption can lead to significant financial losses. The Machine Uptime sensor’s IP65 rating and ability to operate in extreme temperatures (-40 to +60 °C) and humidity (0-90%) conditions make it suitable for the rigorous demands of automotive production lines. Its real-time monitoring capabilities allow for immediate detection of performance deviations, facilitating rapid response to prevent downtime and ensure continuous production flow.
Food Processing Facilities
In the food processing industry, hygiene and safety are paramount. The sensor’s wall-mounted or magnet-mounted IP65 rated enclosure ensures it can withstand the wet and variable temperature environments typical in food processing plants without compromising performance. Moreover, its versatile connectivity options support adherence to strict quality and safety standards by enabling seamless data integration with existing quality management systems.
Chemical and Pharmaceutical Industries
For chemical and pharmaceutical manufacturing, maintaining consistent operational conditions is critical to product quality and compliance with regulatory standards. The Machine Uptime sensor’s encrypted communication and its ability to monitor machinery in real-time provide an extra layer of security and compliance assurance. The sensor’s accurate detection capabilities, including current-based and magnetic field-based measurements, ensure precise monitoring of sensitive production processes, aiding in the early identification of equipment malfunctions that could affect product quality or worker safety.
Mining and Heavy Machinery Operation
The rugged design of the Machine Uptime sensor, combined with its long-range wireless communication capabilities (up to 2 miles), makes it exceptionally well-suited for the harsh and remote environments of mining and heavy machinery operations. Its battery-powered operation allows for easy installation in locations where power sources are not readily available, ensuring continuous monitoring of equipment uptime. This is critical for identifying potential equipment failures before they occur, reducing costly unplanned downtime and enhancing operational efficiency in these industries.
Use-cases
Overall Equipment Effectiveness (OEE)
OEE is a critical metric in manufacturing that evaluates equipment performance by combining availability, performance, and quality factors. In IoT-enabled environments, OEE is enhanced through real-time data collection and analysis, facilitating predictive maintenance and process optimization. IoT devices monitor equipment to automatically calculate OEE scores, predict failures, and identify inefficiencies, enabling proactive adjustments and informed decision-making.
Machine Utilization
Machine utilization measures the effectiveness of industrial equipment by tracking the proportion of time a machine is actively operating against its available time. Enhanced by IoT technology, machine utilization monitoring allows for real-time data collection, enabling more accurate and dynamic assessments of machine performance. IoT sensors gather operational data, helping to pinpoint underutilization issues, streamline production processes, and reduce downtime through timely interventions.
Productivity Measurement
Productivity measurement in industrial settings quantifies the efficiency and output of manufacturing processes. Integrating IoT technology enables real-time tracking and analytics, improving the accuracy and responsiveness of productivity assessments. By collecting data directly from production lines through IoT sensors, companies can immediately detect productivity fluctuations, analyze performance trends, and identify areas needing improvement.
Downtime Tracking
Downtime tracking in manufacturing is crucial for identifying and minimizing periods when equipment is not operational. Enhanced by IoT technology, downtime tracking becomes more precise and automated, allowing for the continuous monitoring of equipment status. IoT sensors can immediately detect when machines halt production and diagnose potential causes, such as mechanical failures or software issues.
- Powered by AA batteries (NCD recommends Energizer L91 batteries)Â
- External power supply (5-12 V DC) Current Requirement 250 mA
Note: The L91 Batteries are non-rechargeable Li-Ion batteries.
While changing the batteries:Â
- Turn off the sensorÂ
- Only use new L91 batteries
- Checkout the polarity marking on the battery holder and batteriesÂ
- Replace all six batteries with new L91 batteries. Do not mix old and new batteriesÂ
- Do NOT install rechargeable batteriesÂ
Note: If these Devices are being used with photo eye or any other sensors needing power, use an external power supply.Â
Most NCD IoT Sensors are rated for 300,000 to 500,000 transmissions until the batteries become so weak they are unreliable. You could spread these transmissions out over a 10 year period and send 50,000 transmissions per year. This would allow up to 136 transmissions per day, or about 5 transmissions per hour (for a 500K sensor, or 3 per hour for 300K sensor). If you only need the batteries to last 3 years, you could send 166,666 transmissions per year, or about 456 transmissions per day (about 19 transmissions per hour for a 500K sensor). As you can see, battery life is really up to you. By altering advanced settings in the NCD IoT sensor, you have control over longevity. Please note the 500,000 transmission rating is for premium alkaline batteries. NCD ships all sensors with premium Lithium batteries, which include a ultra-wide temperature range that typically lasts in excess of 600,000 transmissions for some sensor types. These batteries weigh less than half of alkalines, and they work in the freezer! A word of caution though, putting a sensor in configuration mode will drain the batteries very quickly. It’s important to configure your sensors and exit configuration mode as soon as possible or use a external power supply during configuration (if supported by the sensor). The table below indicates how many Transmissions Per Hour (TPH) your can expect from different sensors over a lifespan of up to 10 years.
The Truth About Battery Life
| Width | 3.54" | |||
| Length | 4.52" | |||
| Height | 2.16" | |||
| Probe Operating Temperature | -40° C | 23° C | 85° C | As Tested by NCD Staff |
| Inputs | Digital, Acceleration, Magnetic, Current | |||
| Opto-input Voltage | 3.3 V | 24V | ||
| Reporting interval | 5 seconds | 600 seconds | 16777215 seconds | How often data is transmitted wirelessly |
| Range of counter values | 1 | 4294967295 | The maximum number of events the sensor can count to | |
| CT Current | 1.5% FS | FS | Minimum current read by the CT. CT range 100 to 1000Amp |
Probes Specifications
There are 4 types of probes: Bare wire for digital inputs, Current sensor, Accelerometer, and Magnetometer.
Digital Inputs
The Industrial Digital Input and Sensor Reader is a compact and robust device tailored to interpret signals from various digital inputs and sensors prevalent in industrial settings, including brake sensors, photo reflectors, and on/off signals. With high accuracy and reliability, it offers real-time data acquisition and monitoring, seamlessly integrating into existing industrial automation systems. Its user-friendly interface and flexible configuration options ensure easy setup and compatibility with diverse applications, enhancing operational efficiency, equipment reliability, and production optimization. Ideal for conveyor systems, packaging machinery, and robotic systems, it empowers industrial operators with streamlined data interpretation and control capabilities, minimizing downtime and maximizing productivity.
When using a digital input sensor the the Rising edge of the pulse is used for the cycle count.
Accelerometer Sensor
The Cycle and Uptime Tracker is an innovative device engineered to monitor and record the number of cycles and total uptime of machinery or equipment in industrial environments. Leveraging advanced acceleration sensing technology, users can set customizable acceleration thresholds to precisely detect cycle initiations. This allows for accurate tracking of machine activity while minimizing false readings. The device captures and stores data, providing insights into equipment usage patterns and overall uptime. With its user-friendly interface and customizable settings, operators can easily configure acceleration thresholds to suit specific machinery requirements. Ideal for diverse industrial applications, the Cycle and Uptime Tracker enhances maintenance planning, optimizes production scheduling, and improves operational efficiency.
Magnetometer Sensor
Magnetic Field-Based Machine On/Off Detection System is meticulously engineered to precisely discern the operational status of machinery that emits magnetic fields during operation. Employing cutting-edge magnetic field sensors, this system offers unparalleled accuracy in identifying whether the machine is active or inactive. With its robust design and reliable performance, there’s no need for user adjustments, ensuring hassle-free operation. Real-time monitoring capabilities enable proactive maintenance planning and energy conservation, enhancing operational efficiency. Seamlessly integrating into various industrial setups, this system represents a pinnacle of reliability and professionalism in machine monitoring solutions.
Current Sensor
Industrial Machine Uptime and Cycle Counter, a cutting-edge solution that accurately measures total machine uptime and cycle counts using advanced current sensor technology. With real-time monitoring and seamless integration, our device enables proactive maintenance planning, enhances operational efficiency, and provides valuable insights for informed decision-making. Upgrade your industrial operations with precise tracking and analysis capabilities for optimized performance and cost savings.
Pin Definition
Getting started
The process is straight forward however you need two components:
- A device to ingest the data, either a DigiMesh modem or a Gateway, we recommend using the IIoT Edge Gateway as it comes with Node-Red pre-installed.
- A working Node-Red instance to process the data (unless using the IIoT Edge Gateway). You can easily install the NCD library by looking it up in your Node-Red Pallet Manager. Search for “ncd-wireless”. Alternately you can manually install it via command line from the following Git repo:Â https://github.com/ncd-io/ncd-red-wireless
For a quick refresher on how to set up your Gateway for the first time, please head to our article on the topic. Once you have it connected to your network and have it set up to connect to the Internet, you can connect directly to its Node-Red instance via the following address:
XX.XX.XX.XX:1880
Where xx.xx.xx.xx stands for the local IP address of the Gateway (for example the one assigned to it via your router, or manually set via its settings) and the port used is 1880 (this is the default for the Node-RED instance running on the NCD Edge gateway).
You need to create the flow from the image below. There are two main components: Wireless Gateway (whether this is the Modem or the IIoT Edge) and Wireless Device (this represent the sensor).
Depending on the particular devices the following settings will differ (the particular example is using the IIoT Edge and a Vibration Sensor). You need to configure the Gateway and the Device to utilize the right interfaces.
If you are unsure on how to c
Let us start with the Gateway.
Double click on the block to see the Properties, enter a name and press on the Pen icon next to the Serial text box to add a new Serial Device.
Give it a name select the appropriate port (depending on what device you are using, you nee to check this for your system). If you press on the magnifying glass a list of ports will be displayed. Select the one right for your use case (the IIoT Edge uses /dev/ttymx2). Select the Baud rate and press the Red button to save it. Press on the Red button again to finalize setting up the Gateway.
Setting up the Device is similar.
Open up the properties and fill in the name. For the Serial Device and the Serial Device for Configuration select the port you just created for the Gateway from the drop down menu. This way data from the sensor will be relayed to the Gateway. Leave the MAC address empty for now (this will ingest data indiscriminately, you can filter it later, the MCA will be displayed in the packets themselves). Select the Sensor Type (in this example 80 – One Channel Vibration Plus. This will allow you to set up Advanced properties.
Check the box for Auto Config and OTF Config. This will allow the device to work in OTF mode where configuration is pushed On The Fly and you can change settings via the Advance parameters further down if need be (the sensor needs to be reset for this).
Close up the window and you are done. Deploy our flow and you should see data being ingested.
Node-RED Dashboard
NCD offers an easy to use solution that you can run locally to display your data. Using the Machine Uptime sensor together with either the Edge Gateway or Edge Lite Gateway if the quickest way to connecting your sensor to a Node-RED instance (they come with a built-in one that is pre-configured).
We have a dedicated tutorial how to utilize our libraries and the flows we have created so you can create a dashboard customized for this particular sensor, follow the link to get started.
Once the Machine Uptime sensor has been powered on and its initial configuration performed you can choose to configure advanced settings/features. This customization is there to allows the user to better tailor the functionality for a specific application/use-case.
In order to better understand how to manipulate the device settings we need to explain its 2 operational modes in detail. These modes are:
This is the default mode and the device enters into it when it is Powered-up/Reset unless a button is pressed. In this mode the device sends regular uplinks and acts in accordance with the configuration parameters unless changed.
This is a temporary mode that is not intended for long-term operation. The device goes out of it an back to Run Mode after every Reset/Power cycle. It is intended to adjust the sensor parameter values. You can enter in this mode by pressing the CFG button while resetting the device (refer to the graph below for the precise timing of the CFG button press).
Note: The device checks every hour for configuration changes and automatically updates its settings, you need not physically interact with it to update it!
CFG Button timings
- <2 second – device starts normally in RUN Mode
- >15 seconds – the device reverts back to the Factory Default Settings, which is followed by a Configuration Mode Frame
Note: Pressing the button while the Machine Uptime device is running does no change modes, it needs to be reset (either via the Reset Button or Power Cycling). In order for the new settings to apply the devices needs to be Reset.
Factory Default/Reset
In case you have are in need to revert to the default settings (>15 seconds of CFG Button press when Reset), you can utilize the following table to look up their values. This will be implemented once the device has been reset (post Configuration mode).
Note: Post factory reset the sensor will be sending frames with the default interval of 600 seconds (every 10 minutes).
| Parameters | Value set |
| Node ID | 0 |
| Delay | 600 (DEC) seconds |
| PAN ID | 7F FF (HEX) |
| Key | {85,170,85,170,85,170,85,170,85,170,85,170,85,170,85,170} (DEC) |
| Encryption | Enabled |
| Change Detection | Enabled |
| Change Detection Percentage | 10% |
| Change Detection Time | 7 seconds |
When the Machine Uptime device powers up, depending on the mode it is going to work in, it will have a different Power Up FrameÂ
Note:Â Right after factory reset the sensor enters configuration mode therefore its PAN ID is changed again and a new frame is generated.Â
| 8 | 0x55 | |||
| 9 | 0x4E | |||
| 8 | 0x47 | |||
| 9 | 0x4D | |||
| 8 | 0x55 | |||
| 9 | 0x4D |
Run Mode Power Up Frame
| 0x7E | 1 | Delimiter |
| 0x001C | 2 | Length |
| 0xFFFE | 2 | Reserved |
| 0x00 | 1 | R. Option |
| 0x01 | 1 | Node ID |
| 0x00 | 1 | Separator |
| 0x0001 | 2 | Sensor Type |
| 0x0000 | 2 | Separator |
| 0x0B | 1 | Checksum |
| 0x0E | 1 | Checksum |
Run mode is the default mode of operation of this sensor. In this mode, the Machine Uptime sensor sends periodic packets with the sensor measurement data. During the time it is not sending it enters deep-sleep to conserve power. The sensor’s X-bee module operates in API mode and sends packets to the saved destination address on the network specified by the saved PAN ID. Figure 4 illustrates the API transmission/reception procedure.
Note: The communication works in confirmed mode, meaning that acknowledgements are received for each transmitted packet. In case no acknowledgement is received for a packet, the device retransmits the packet up to 3 time in an attempt to successfully send it over. This is part of the X-bee API functionality and is built-in (does not need to be user coded).
The detail of Payload section of packet is shown in Table 3 below:
| Frame Field | Offset (Payload section) | Fixed Value (if any) | Description |
| Header | 0 | 0x0F | Header to differentiate various types of packets |
| Node ID | 1 | 0x00 (Factory Default) | Node ID to differentiate up to 256 nodes in a network. User configurable values |
| Firmware | 2 | 01 | Used to determine firmware version programmed in the device |
| Battery Voltage | MSB 3 | 03 | Battery Voltage = 0.00322*(03*FF+FE) |
| LSB 4 | FE | Battery Voltage = ((Battery Voltage MSV x 256) + Battery Voltage LSB) x 0.00322 V | |
| Packet Counter | 5 | - | It is an 8-bit counter that increments with each packet transmission. It can be used to detect missing packets |
| Sensor Type | MSB 6 | 0x00 | Two bytes to determine sensor type. It can be used in conjunction with Node ID to create sensor networks of up to 256 nodes for a single type of sensor and multiple such networks can coexist and can be differentiated in processing software on PC end. |
| LSB 7 | 0x6C | Sensor type 108 | |
| Error/Reserved byte | 8 | 0x00 | For future use |
| Digital Input 1 Counter | D2,D3,D4,D5 | - | Counter 1 = D2 << 24 | D3 << 16 | << D4 << 8 | D5 |
| Digital Input 1 Uptimer | D6,D7,D8,D9 | - | Uptimer 1 = D6 << 24 | D7 << 16 | << D8 << 8 | D9 |
| Digital Input 2 Counter | D10,D11,D12,D13 | - | Counter 2 = D10 << 24 | D11 << 16 | << D12 << 8 | D13 |
| Digital Input 2 Uptimer | D14,D15,D16,D17 | - | Uptimer 2 = D14 << 24 | D15 << 16 | << D16 << 8 | D17 |
| Digital Input 3 Counter | D18,D19,D20,D21 | - | Counter 3 = D18 << 24 | D19 << 16 | << D20 << 8 | D21 |
| Digital Input 3 Uptimer | D22,D23,D24,D25 | - | Uptimer 3 = D22 << 24 | D23 << 16 | << D24 << 8 | D25 |
| Accelerometer Counter | D26,D27,D28,D29 | - | Accelero Counter = D26 << 24 | D27<< 16 | << D28 << 8 | D29 |
| Accelerometer Uptimer | D30,D31,D32,D33 | - | Accelero Uptimer = D30 << 24 | D31 << 16 | << D32 << 8 | D33 |
| Magnetometer Counter | D34,D35,D36,D37 | - | Magneto Counter = D34 << 24 | D35<< 16 | << D36 << 8 | D37 |
| Magnetometer Uptimer | D38,D39,D40,D41 | - | Magneto Uptimer = D38<< 24 | D39 << 16 | << D40 << 8 | D41 |
Configuration Mode (enter via CFG key press) is intended to setup the device over the wireless link, you can change parameter values that are subject to change via downlink commands.
In configuration mode, the device sets its X-bee pan id to 7BCD (Table 2). Also, the destination address used by the sensor is extracted from the incoming packet (source address). This ensures that once you put a device in configuration mode you just need to change the PAN ID you are sending to in your Modem/Gateway to match with the sensor and start configuring your device.
A standard configuration packet and its fields are explained in Figure 5. Its possible responses are also shown. The complete set of commands supported by this sensor are shown in Appendix A, these can be used in the Parameters field of the Payload section. The sensor responds to these commands with an acknowledgement if the process completed successfully or with an error if it failed to setup a parameter. The respective Data and Reserve section length and values are shown in Table 6 for the case of acknowledgement. In the case of error, the reserved section will be fixed and not used, while the Error number byte will determine the type of error returned. These errors are mentioned in Table 7.
Note: Sensor commands have variable length frames whereas responses received from sensor are fixed length. The 2 scenarios are also shown, where a command can result in an acknowledgement reception or an error reception.
The following set of commands are an example on how to change some of the parameters that affect the operation of the Machine Uptime device (these are parameters that are general in nature, more on a network protocol/device level than device specific). The relate to settings that are independent of the type of probe used. You can find them in Appendix A as well.
Device/Application Specific command you can find in Appendix C.
Read Sleep Duration
Read Sleep Duration Command
00 00 00 00 00 00 FF FF
A. Sensor MAC address
00 13 A2 00 41 91 1B 83
B. Sensor Over-all Payload
C. Delay Value
Payload
F7 02 00 00 00 01 00 01 2CÂ Â
A. Node ID
0x01 (Byte 23)
B. New Delay Value
A. Sensor MAC Address
B. Complete Sensor Payload
C. Network ID
0x07FF (data bytes 23 and 24)
F7 05 00 00 00 7C DE
0x0000FFFF
A. Complete Sensor Payload
B. Sensor MAC address
C. Destination Address
Complete Payload
F7 03 00 00 00 12 34 56 78Â
Complete Payload
F7 01 00 00 00
Read Sensor Power Command:
B. Sensor PayloadÂ
C. Power Level
0x04 (data byte 23)
B. Complete Sensor PayloadÂ
C. Retries Number
0x0A (data byte 23)
Complete Payload
F7 06 00 00 00 05Â
Complete Payload
| 15 | Set Change Detection Parameters | 0XF7 | 0x07 | E, PR, T0 MSB, T1, T2 LSB | Enable or disable the percentage change detection. E=1 (Enable), E=0 (Disable) PR is the percentage change detection at which the sensor will send a packet. The sensor sends a packet when two consecutive readings differ by PR percent T0, T1, T2 - This is the detection time after which the sensor periodically checks for PR percent change in sensor data from last sample |
| 16 | Read Change Detection Parameters | 0XF7 | 0x1A | - | Refer to Command 15 above for the explanation. |
| 14 | Set Encryption Key | 1 | 8 | 0xFF (OK) | |
| 15 | Set Change Detection Parameters | 1 | 8 | 0xFF (OK) | |
| 16 | Read Change Detection Parameters | 5 | 4 | E, PR, T0, T1, T2 | Detection time = (T0 x 65536) + (T1 x 256) + T2 |
| COMMAND | COMMAND | SUB COMMAND | Reserve Byte | COMMAND CODE | ARGUMENT |
| SET Acceleration Threshold | 0xF4 | 0x20 | 0x00,0x00,0x00 | 0x14 | This example command will set the acceleration threshold to 20*32mg = 640mg |
| GET Acceleration Threshold | 0xF4 | 0x21 | 0x00,0x00,0x00 | ||
| Clear all counters | 0xF4 | 0x24 | 0x00,0x00,0x00 | 0x1F | Reset all counter values to 0 |
| Clear Accelerometer Counter | 0xF4 | 0x24 | 0x00,0x00,0x00 | 0x08 | Reset Acc counter values to 0 |
| Clear Magneto Counter | 0xF4 | 0x24 | 0x00,0x00,0x00 | 0x10 | Reset AMag counter values to 0 |
| Activate Accelerometer | 0xF4 | 0x25 | 0x00,0x00,0x00 | 0x01 | Activate Accelerometer |
| De-Activate Accelerometer | 0xF4 | 0x25 | 0x00,0x00,0x00 | 0x00 | De-Activate Accelerometer |
| Set Debounce Time | 0xF4 | 0x27 | 0x00,0x00,0x00 | 0x64 | This will set debounce value to 100msec |
| Get Debounce Time | 0xF4 | 0x28 | 0x00,0x00,0x00 | read stored debounce time Value |
| 0x01 | Invalid command |
| 0x03 | Node ID mismatch |
Calculation for transmission
0x04
0xFF-0x04=0xFB
Calculation for reception
0xFF
